I would be grateful if someone help me on this clarification please.
Wastewater pumping station: I understand that the ACQ580 ABB Drive can be used to control wastewater pumping station using an ultrasonic level transmitter (4-20 mA) and using the multipump function.
My query is that if the transmitter fail i.e. there is a loss of the analogue input on the ACQ580, this may cause an overflow or is there another function available such as a high level float switch that may be configured as backup to start the vsd. |
|
| Back to top |
|
 |
0day Member junior

Joined: 09 Dec 2017 Posts: 54
|
Posted: 27/05/2019 21:39 Post subject: |
|
|
Normally the technological engineer in wastewater must provide or a way to evacuate overflow or as you already say there must be a set of min max sensors for Emergency STOP depending the situation.
If the situation is critical the min max sensors has to be entered into a define state just in case there are a defective sensors. And more, the PLCs from waste water station must be linked in a redundant ring.
 |
|