10kW 3-Phase 3-Level Grid Tie Inverter Reference Estetică for Solar String Inverter
This verified reference stil provides an overview on how to implement a three-level three-phase SiC based DC:AC grid-tie inverter stage. Higher switching frequency of 50KHz reduces the size of magnetics for the filter design and enables higher power density. The use of SiC MOSFETs with switching loss ensures higher DC bus voltages of up to 1000V and lower switching losses with a peak efficiency of 99 percent. This design is configurable to work as a two-level or three-level inverter.
http://www.ti.com/tool/TIDA-01606
Rated nominal/max input voltage at 800V/1000VDC
Max 10kW/10KVA output power at 400VAC 50/60Hz grid-tie connection
Operating power factor range from 0.7lag to 0.7lead
High voltage (1200V) SiCMosFET based full bridge inverter for peak efficiency of 99%
<2% output current THD at full load
Isolated current sensing using AMC1301 for load current monitoring
Isolated driver ISO5852S with reinforced isolation for driving High voltage SiC MOSFET and UCC5320S for driving middle Si IGBT